Anybody has any idea how to calculate the acceleration of a Composite steel deck supported by joists that at the same time are supported on CMU or Reinforced concrete walls?

It's not taken into consideration in the Design Guide examples and I don't know if assuming the wall is a deep beam would be permissible or if in any case it'd either reduce the accelerations to a permissible level. Murray's software supposedly does take into account the walls but the Design guide doesn't really mention it. I'm trying to write a program in python to carry out this automatically (based on floorvibe, with a similar GUI)and drawing information directly from AISC shape and Joist institute's database.

ANyhoo, I hope somebody can point me in the right direction, thanks !!!

RE: Vibration analysis using AISC Design Guide 11 when supported on walls

In the case of wall supports or other very stiff members, they are assumed to have an a/g = 0. You would check the vibration of the system for the joist mode only and would not need to check the girder or combined joist/girder modes.

RE: Vibration analysis using AISC Design Guide 11 when supported on walls

(OP)
Oh I see, thanks for your prompt reply and I have another questions for you :). When it comes to the damping coefficient am I permitted to augment the limit above 5% or just set the value at the limit (I would assume presence of walls would be somewhat effective in damping vibrations)? I mention this because of the building I was working on earlier, I had some software by Murray that was based on the old provisions where the heel-drop acceleration was the one to rule but augmenting the weight of the floor, augmenting c. to c. distances of joists was just not cutting it, I'd end up with really deep and heavy floor systems. I just read an article by Murray and he said that they old provisions were really off and designs should be using the new provisions but his software it's not really simple to use, I think it is best when it's used in conjunction with RAM. So I'm testing my luck to see if I can create something more useful and easier to use.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources