ASME Section I Overpressure for a single PSV

ASME Section I Overpressure for a single PSV

ASME Section I Overpressure for a single PSV

(OP)
Dears,

Referring to the thread1203-196378: ASME Section 1 Overpressure i think for a single PSV in ASME Section I application, 6% overpressure respect to the set pressure could be applied provided that the relieving pressure not to be more than 6% above the maximum allowable working pressure. What is your opinion?...

RE: ASME Section I Overpressure for a single PSV

For the boiler?

RE: ASME Section I Overpressure for a single PSV

A 400 psi boiler requires a 400 psi PSV. AFTER the PSV lifts at the MAWP, then some pressure accumulation above the 400 psi MAWP is allowed. You do not get to start above the MAWP, and hope that you will not exceed the allowable accumulation pressure.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources