I have a prospective client from Germany who wants to do a detail I am unfamiliar with in the States. He says they buildA photo is attached showing the concept. Basically your veneer stands proud of the structure, as much as 6". This 6" void is filled with fiberglass insulation. The veneer is tied back with a system of periodically spaced masonry ties. The problems with this that jump to my mind are:

- buckling of the ties under compression (direct wind)
- seismic loads on the veneer would make the entire tie system try to pancake as the veneer sways back and forth parallel to the wall
- squishy......the insulation has zero compressive resistance. Perhaps if it was rigid foam? Or if we had ties with compression ability?

This is just a strange detail to me, and I'll admit that part of that is because I have never seen it before. Any input from people who have used this or had success (or failure) with this would be great.

RE: Strange Brick-Insulation Detail.....Euro Method?

(OP)
Sorry for the typ-0. Hit post instead of edit.....I was saying that apparently this detail is very common in Europe, per this builders experience.

RE: Strange Brick-Insulation Detail.....Euro Method?

That is very normal in the states as well. I would not use fiberglass insulation as it will absorb water, use closed cell polyiso board. I have done many brick veneers, you tie the bricks back to the structure with clips at a dense spacing (clips at 24" o.c. horiz and 16" o.c. vertical). This is in the IBC Building Code as a minimum steel area per square foot basis. In high seismic zones you use special Seismic Anchors ties that account for the loads. Look into Hohmann & Barnard brick ties: (http://www.h-b.com).

Please note that your photo also does not show a vapor/moisture barrier (or air barrier if a large commercial project). And i would never use those ties, they look bad... Basically that photo is illustrating an example; but in my opinion is a very poor design.

Remember brick is a poor weather barrier, it is porous, it will leak, it will crack, and it is heavy. But it does look nice! So i guess at 40psf leaking whats the problem :)

RE: Strange Brick-Insulation Detail.....Euro Method?

This should show you something that works for you.
http://www.h-b.com/index.php?main_page=product_inf...

I have done wall cavities up to 6" but they are hard. Anything over 4" cavity causes headaches with fixed lintels and shelves. And you can typically get a good R value with spray foam/board

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources