Built-up steel beam with different yield strengths
Built-up steel beam with different yield strengths
(OP)
Someone double check my logic here:
Reinforcement of a existing steel wide flange beam, yield strength of 50 ksi. Will be done by welding 36 ksi cover plates on the flanges. For the plastic (Zx) allowable moment I should be able to calculate the plastic section modulus for the beam and plates separately and multiply them by their respective yield strengths and then add the two moments together, correct?
For the cases where lateral torsional buckling, compression flange buckling, correct?
For tension flange yielding I can use the Sx of the tension flange multiplied by the yield strength of the flange added to the Sx of the tension plate multiplied by the plate's yield strength, correct?
Any papers or examples that cover this situation that anyone can point me to would be a great help. Couldn't find anything that specifically covered this situation.
Reinforcement of a existing steel wide flange beam, yield strength of 50 ksi. Will be done by welding 36 ksi cover plates on the flanges. For the plastic (Zx) allowable moment I should be able to calculate the plastic section modulus for the beam and plates separately and multiply them by their respective yield strengths and then add the two moments together, correct?
For the cases where lateral torsional buckling, compression flange buckling, correct?
For tension flange yielding I can use the Sx of the tension flange multiplied by the yield strength of the flange added to the Sx of the tension plate multiplied by the plate's yield strength, correct?
Any papers or examples that cover this situation that anyone can point me to would be a great help. Couldn't find anything that specifically covered this situation.
Maine EIT, Civil/Structural.






RE: Built-up steel beam with different yield strengths
RE: Built-up steel beam with different yield strengths
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
"For the cases of lateral torsional buckling and compression flange buckling I should just use the yield strength of the outermost section (the plates in this case), correct?"
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
RE: Built-up steel beam with different yield strengths
I likely would use 36 ksi for the lateral and buckling checks and see where I ended up first.
RE: Built-up steel beam with different yield strengths
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
Yes, so long as the composite section remains symmetric. I typically use a wider plate on the bottom.
I don't think this is correct. The beam section won't be yielded when the reinforcing plates yield at the extreme fibre (My). Alternately, if you don't jack the beam to relieve internal stress, the beam flange may yield before the reinforcing plate does.
This is the tricky part. Certainly, assuming 36 ksi would be more conservative than 50 ksi. Even that might not be conservative enough in all situations however. The underlying principle is that, at the development of the desired moment capacity, enough of the cross section must remain elastic that you can count on it for torsional stiffness (Iy & Cw). Two basic scenarios:
1) You jack to relieve all stresses before reinforcing. In this case, you can safely use the larger of a) 36 ksi and the combined section properties or b) 50 ksi and only the W-beam section torsion properties, assuming that the plates yield early in the load history.
2) You don't jack to relieve stresses before reinforcing. In this case, you don't know which part yields first unless you do some detailed calcs. You can safely use the lesser a) 36 ksi and the torsion section properties of the reinforcing plates alone and b) 50 ksi and the torsion section properties of the beam section alone.
For both scenarios, you could probably get more capacity by working out state of yielding in the combined section and proceeding accordingly. Too much work for routine design unless you've got a spreadsheet to help.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Built-up steel beam with different yield strengths
I'll look for it but only found this from back in 2009: http://www.eng-tips.com/viewthread.cfm?qid=243663
If it wasn't symmetric would it matter? As long as my calculation of the plastic neutral axis and the resulting Zx for the plates and beam were consistent with the single symmetric beam it should still work to sum the two plastic section modulus values, right?
I'll probably just make the conservative assumption that the lowest yield strength controls. I would be surprised if tension yeilding controlled in most typical designs anyway.
I've read a lot and can't find any agreement on wither shoring to remove the stress needs to occur. Obviously deflection control needs shoring but as best I can find you don't have to shore if you're reinforcing for strength. Here's a PDF presentation from Larry S. Muir on Rehabilitation of Existing Structures where he states that shoring is not required for strength reinforcement of beams: http://www.larrymuir.com/Documents/Existing%20Stru...
Yep, making a spreadsheet is what caused this discussion.
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
As long as the composite section plastic centroid coincides with the w-beam plastic centroid, you're good. Otherwise, not good.
Regardless of what you use for Fy, your My calc will be incorrect unless you use the Sx of the composite section. You can't split it out into the W-Beam + Reinforcing plates like you can with Zx. The difference may not be all that significant however.
You can do as you please so long as your analysis is consistent with your choice. I avoid jacking whenever possible. Once you factor in the tolerances of jacking it just so, you get diminishing returns anyhow. Thanks for the paper. That's a new one for me.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Built-up steel beam with different yield strengths
RE: Built-up steel beam with different yield strengths
RE: Built-up steel beam with different yield strengths
My guess is that you must glean LTB stiffness from:
1) The stiffness of the unloading curve for the portion of the compression flange that gets it's compression reduced.
2) Eventual strain hardening of the portion of the compression flange that gets its compression increased.
3) Maybe some tidbits here and there from the original residual stress pattern.
How to assess that? Who the heck knows...
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Built-up steel beam with different yield strengths
RE: Built-up steel beam with different yield strengths
Imagine starting with a 36 ksi section where the flange is stressed to 80% Fy. Now add some 36 ksi reinforcing plates. By the time that you yield the reinforcing plate, the original flange may be so far along the yield curve that it will posses no Iy/Cw of its own. In this case, I'd argue that Iy and Cw should be based on the reinforcing plates alone.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Built-up steel beam with different yield strengths
Hokie93: Nice! I'm usually on top of the AISC articles, thanks for the link. I was working nights at a job site the entire month of October and then took the lateral portion of the SE exam on the 25th. I kind of don't remember what happened during that time and probably missed a lot of my usual reading. :)
canwesteng: Great point and also backed up by Hokie's article. I forgot that the inelastic LTB isn't a straight line like the steel book assumes, great point. I'll definitely use 36 ksi for LTB.
In conclusion I think that I should conservatively assume the lower yield strength for all limit states. This makes the most sense as it avoids the extreme complication of figuring out flange compression, tension, and LTB for the two yield stresses. If I did indeed want maximum reinforcement then the plastic moment is the way to go and it does appear possible (if somewhat complicated) to find the actual plastic moment capacity. However, as KootK pointed out it becomes much more challenging to find the plastic moment capacity if the PNA is not the same between the 36 ksi and 50 ksi pieces. Add to this that some amount of capacity may be lost without shoring the beam up to remove dead load stresses.
Thanks for all the great advice, I'll modify my spreadsheet to use the lower Fy of the design plates and beams.
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
Michael.
"Science adjusts its views based on what's observed. Faith is the denial of observation so that belief can be preserved." ~ Tim Minchin
RE: Built-up steel beam with different yield strengths
I still haven't found any testing data on this though. I'm sure it's out there but haven't found it yet.
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
I've been working off of a similar premise for columns for a few years now. I've found that most column reinforcement comes down to improving buckling resistance by increasing flexural stiffness. For that, as long as the original column doesn't exceed it's squash load, it doesn't really matter whether or not the axial load is shared between the original column and the reinforcing.
I'd be careful assuming that the loaded/unloaded thing doesn't matter for beams however. In Larry's presentation, he specifically references floor beams. Typically, such beams are simply supported and well braced enough that LTB is not a concern. I haven't done the paper reading yet, but my intuition is that locked in stress will still matter whenever buckling matters.
This whole business of steel being awesome at load redistribution has always given me pause for concern. A while back, I read Tamboli's book on steel connections for which Muir was a contributor. The fundamental theorem of steel connections is stated, at the very beginning, as something to the tune of "we never really know the loads but, as long as everything is ductile, it doesn't matter". Unfortunately, buckling is not ductile (more so for plates obviously). So, every time that you've got a Whitmore section in compression, that fundamental theory is bunk. Welds, also, are not terribly ductile. I believe that's the idea behind the 1.25 factor that we tack on from time to time.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Built-up steel beam with different yield strengths
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: Built-up steel beam with different yield strengths
Good point on the distinction of floor beams. The Steel Interchange October 2014 article that Hokie mentioned also had a discussion on design of curved lifting beams on the same page. I just happened to read it and it's also applicable. Link is here: http://msc.aisc.org/globalassets/modern-steel/arch...
The important point it mentions, similar to your point, is "generally, residual stresses have no effect on the ultimate strength of a member but can affect stability." They point out that typically the built-in stresses in a rolled vs. unrolled beam will be at similar levels. They state that the AISC specification uses 20% to 80% as the assumed compression flange residual stresses and thus rolling a beam doesn't cause stability issues alone.
For beam/column reinforcement it appears prudent that unless you can reduce your beam/column stresses below 80 percent then you may have buckling issues. I gather this is more or less what you were saying above, if you have a beam at 100% flexural stress then there's very little buckling capacity (Iy/Cw) left in the flanges and as such buckling should be considered when reinforcement is applied. Thankfully about 99% of the time we can remove all but dead load from beams being reinforced so I imagine this typically isn't an issue but I will definitely include this check in my spreadsheet.
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
Maine EIT, Civil/Structural.
RE: Built-up steel beam with different yield strengths
1) What are the existing live/dead loads,
2) That the field conditions will allow the modifications to be done properly.
It may look simple to meet these assumptions. But I have dealt with having to do to many changes to my repair designs, to refine any field repairs so much in the beginning.
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: Built-up steel beam with different yield strengths
In the end for other reasons I'm not going to consider differing yield stresses in the spreadsheet but you're right that often dead and live loads are not well known. I would put forward that as long as it's well below the point where buckling controls that it such variability can probably be ignored. You could also justify that this variability is already accounted for in the safety factors.
Maine EIT, Civil/Structural.