Fuses as back up protection?

Fuses as back up protection?

Fuses as back up protection?

(OP)
Normally the loss of distribution feeders from stuck breakers or relays failures is mitigated by a double breaker-double buss or a breaker and a half scheme.

Smaller/ older substations are single breaker single buss, so if one breaker fails the entire buss is lost as well as all outgoing feeders. Is it possible, or practical, to add power fuses in series with the breakers to avoid such a contingency?


RE: Fuses as back up protection?

If the fuse can be coordinated.

I don't find this possible at higher fault currents.

RE: Fuses as back up protection?

It would also complicate any reclosing sequence quite a bit.

RE: Fuses as back up protection?

Suck it up and change your reclosing sequence.

RE: Fuses as back up protection?

Also may interfere with proper operation of any directional relaying?

RE: Fuses as back up protection?

You are essentially putting in one more series overcurrent device to coordinate. The fuse will have to be slower than the feeder overcurrent relay and faster than the backup (main bus breaker?) overcurrent relay. It is often difficult to coordinate overcurrent relays without adding an extra device. If you use a fast bus scheme (zone interlocking) for bus protection, the fuse won't act fast enough to prevent a bus trip.

RE: Fuses as back up protection?

(OP)
I might go with zone interlocking or transfer trip type logic. Worse come to worse I can set the transformer secondary buss feed breaker to a higher inverse time current curve level.


The other option, and Im not sure how to get it to work is motorized air breaks... Basically is a feeder breaker fails to trip, the main buss breaker will trip. The effected circuit will sectionalize via air breaks and once having done so the main buss breaker will reclose. However, from a relaying standpoint I have little idea how to go about it as the distribution level.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources