CT connection/configuration

CT connection/configuration

RE: CT connection/configuration

That's about the only way that you can retrofit a modern relay into old switchgear that never had a B-phase CT. Not great, but it works; a resistance grounded system helps.

RE: CT connection/configuration

(OP)
Let me ask you this, do you have a reference that supports this ct config? i havent been able to find one in my references.

RE: CT connection/configuration

It's recommended by SEL for these situations. We have used this multiple times and it does work. Just make sure both the CTs have the same ratio. That has come up once on some older switchgear.

RE: CT connection/configuration

What kind of reference? I've seen it before. Assuming low ground fault currents (resistance grounded system), then Ib = -(Ia + Ic) and that's what that wiring achieves. That relay is replacing two phase relays and one ground relay. If you don't connect anything to the Ib inputs the relay will see a standing residual current.

RE: CT connection/configuration

(OP)
ok, thanks for your input. appreciate it

RE: CT connection/configuration

(OP)
mostly david i was looking for a industry standard configuration to defend that wiring config to go along with the pdf description of what i was planning on doing

RE: CT connection/configuration

The most common place I've seen the 2-CT wiring is in the instruction manuals of some digital 3-phase panel meters such as a Tyco Integra or Accuenergy meter.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources