Biaxial Bending in Concrete Beams
Can anybody give me some insight on how to handle biaxial bending in concrete beams. The Beam doesn't have any axial load...just bending in 2 directions. How do you account for the combined bending. I can't find anything in the ACI except for columns with Biaxial bending and axial load. Any help would be appreciated. Thanks
RE: Biaxial Bending in Concrete Beams
I would size the top and bottom reinforcing bars of the beam for the vertical moment, and the side rebars for the horizontal moment. I would count the corner bars only as 1/2 bar because one corner rebar may be stressed by both moments.
Similarly, I would design the shear ties in such way that they provide the shear reinforcement required by each loading direction. I would use only 70% of the concrete shear strength (Vc) to account for the skew direction of the shear force.
This method may not be theoretically exact, but it is simple and, I believe, is conservative.
AEF
Here you would probably have substantial overlap of the 2 compression zones, so you should add the compressive stresses.
And as the previous reader eluded too rotating the n.a. is how the program generates the 3D interaction diagram. From the 3D diagram 2D interaction diagrams are extracted.
Also in some older version of ACI codes there are short cut methods using combined stress ratios (interaction equations). They are very conservative. Using the above program is easier and more economical.
later,
John
PS: If there are any questions I can be emailed a southardengineering@yahoo.com
I am no structural engineer but I wondered, assuming that the loads on the beam were through the neutral axis and at right angles to each other could you not use the principle of superposition ie:- calculate stresses and deflection for
the beam taking each load seperately.
regards
desertfox