Reduced Beam section Special moment steel frames
In the protected zone of an RBS special moment connection, we are not allowed to attach to the flanges. What about the web? Can we attach to the web within the protected zone w/bolted steel angles to pick up a framing members? I checked with FEMA books and AISC seismic manual, there was no mention of web. All the reference material has to do with flanges.
Can some one shed some light?
Thanks in advance.
Thanks in advance.
RE: Reduced Beam section Special moment steel frames
See AISC 358-10 general protected zone requirements in section 2.6
"Bolt holes in beam webs, when detailed in accordance with the individual connection provisions of this Standard, shall be permitted."
For RBS, see section 5.6.(2)(a)
"Bolt holes in the beam web for the purpose of erection are permitted."
The extents of an RBS protected zone is defined in AISC 358-10 section 5.3.1.(8):
"The protected zone shall consist of the portion of beam between the face of the column and the end of the reduced beam section cut farthest from the face of the column"
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.