3 Phase electric power and load calculation
hi....
i want to know the formula for calculation of 3 phase load(kva) in real life.i have current load values on 3 phases which are different as 56amp,42amp,40amp. Voltage line to neutral is 220v and line to line is 380v.do i use 3 or root(3) or nothing in the formula.how can i calculate load on one phase and total load on all the three pahses in 3 phase system
RE: 3 Phase electric power and load calculation
For a balanced wye connected
load only:
P = 1.732 x VL x IL
in your case the load is not balanced so do the loads individually and add them up like magoo2 suggested.
56A x .22kv (phase A) + 42A x .22kv (phase B)+ 40A x .22kv (phase C)
If the load was balanced and the line current for example was 50A
P = 1.732 X 50A X .38kv
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
OK, if we're going to pass out equations, let's try to be accurate. If P = Power, you forgot to account for the power factor. I have enough aggravation with non-EEs on this.
