Dear all,

I have a project in which a Genset has to feed a 20kV line. My first option is to use a step down transformer in reverse feeding connection. I am waiting your comments on this solution.

Thanks in advance.

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

The transformer doesn't care what direction the power is going. There are some subtle differences in transformer designed specifically for generator step-up applications, but a standard transformer will work fine.

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

(OP)
Hi dpc,
thank you for your reply. Can you send me a table with these differences ?

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

If I am not mistaken inrush may be greater if reverse fed.

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

(OP)
Mbrooke you are right. Inrush current is greater. Moreover if you have 1-Phase loads currents will be in neutral. This will be a problem if you have Dyn solidly grounded transformer, but I am waiting for further information ...

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

I don't have a table. I'd recommend talking to a transformer manufacturer if you have further concerns.

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

Worry less about the transformer, and worry more about system grounding and protection for faults on your 20kV line.

Regards
Marmite

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

(OP)
Marmite, do you mean L-G fault? Do you believe that I should use a "special" protection ?

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

I agree with marmite, line to gnd fault on the 20 kv line is probably the biggest concern. I assume that the line would have some kind of effective grounding, and an ungrounded source is introduced by connecting a generator through a transformer with delta primary. Your line protection should trip the transformer or the generator (depending on the configuration) on any line fault and an open corner delta or similar neutral displacement protection could be used as a backup.

RE: Reverse feeding power transformer 1250kVA 20/0.4kV Dyn11

(OP)
Borti, can you send me more details ?

Thanks

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources