a building is located with the fire zone of big power transformer (15 m) . The recommendation of fire rated design is achieved however the architect would like to put some windows into the subject walls. NFPA 850 recommends using automated louvers for such windows but no one will be happy with extra cost.
The transformer is protected by water spray system as an active FF. Does the introduction of such active FF system help reducing the required 15 m passive distance?
The transformer is protected by water spray system as an active FF. Does the introduction of such active FF system help reducing the required 15 m passive distance?





RE: Power Transformer Fire
RE: Power Transformer Fire
RE: Power Transformer Fire
RE: Power Transformer Fire
As to the use of a water spray system in lieu of separation distance, it's not possible to respond to the questions because the volume of oil isn't stipulated. From my cursory glance at NFPA 850, one can apply engineering judgement for transformers < 500 gallons of heat transfer oil for smaller installations and you may be able to justify the water spray system as a credible reduction variable. Installations = or > 500 gallons should follow the prescriptive spatial separation distances unless they transformer is separated from the exposure by a two-hour fire barrier designed in accordance with NFPA 850, Section 5.1.1.4.