Is a generator step up transformer typically specified for hydroelectric generators in the 10 MVA range or is a standard distribution transformer typically applied? I understand that GSU transformers have different specifications for power flow in the reverse direction for large generators but I am not sure if the units are even available in this power range.






RE: GSU Transformer for 10 MVA Hydropower Unit?
RE: GSU Transformer for 10 MVA Hydropower Unit?
RE: GSU Transformer for 10 MVA Hydropower Unit?
RE: GSU Transformer for 10 MVA Hydropower Unit?
I think those are the questions being implied.
There should be little difference between a GSU or any other transformer, unless you specify a condition of use that is not normal. The condition of use would be something like high harmonic, or alitutude, or cooling, or tempeture range.
RE: GSU Transformer for 10 MVA Hydropower Unit?
Instead of tie transformer, why not connect the generator directly to 13.8 bus by a standard Yd GSU ?