I have VTs of A, b, and C phases to be connected open-delta. The ratios are 115/3 for both A & B phases and 115 for C phase. What will be the effect and what can I do?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Open-delta connection
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Open-delta connection
(2) It was to be used for 64N protection
RE: Open-delta connection
RE: Open-delta connection
In North America an open delta is as davidbeach has described; two transformers used for delivery of three phase power for generally small loads.
In Europe an open delta is three transformers in delta with one corner of the delta open. This connection is called a broken delta in north America. For this connection you must start with three transformers with equal ratios. It is not a good idea to mix 115 Volt transformers with 3 Volt transformers.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Open-delta connection
It is not a good idea, but if it happen, what will be the effect? 115/root3 for A & B phases and 115 for C phase
RE: Open-delta connection
RE: Open-delta connection