MG book states that TT system isn't allowed to supply places with high fire risk, but doesn't give any reason, is there any?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
TT system in fire risk environment
|
RE: TT system in fire risk environment
What do you mean by MG book?
On a TT system if earth fault protection is provided by residual devices such as Current Operated Earth Leakage Circuit breakers
(ELCBs/ RCCBs) with 30mA trip threshold then there cannot be a fire risk. But if you provide earth leakage protection by overcurrent
devices then there can be a fire risk because the earth leakage current may not be enough to trip the overcurrent devices unless
you make sure that the "measured" earth fault loop impedance is less than 1666 OHMS to satisfy the allowable touch voltage
of 50V per IEC for 30mA threshold.
RE: TT system in fire risk environment
on other hand, why TN-C is not allowed in a risk of fire?
RE: TT system in fire risk environment
Due to high earth fault currents RCD devices are not allowed in TN-C systems. Per IEC60364, in a TN-C earthing system the earth fault current is
taken back to the source by the PEN conductor in contrast to PE conductor of a TN-C-S earthing system. That means at each utilization equipment,
the N terminal has to be bonded to the E terminal. With time if this bonding develops a high resistance to the earth fault loop impedance then,
the tripping time of the overcurrent device during an earth fault will be longer (more energy is released at the fault point) and it might
create a fire within the installation. Therefore, at installations or buildings where there is a fire risk, TN-C earthing is not acceptable.