Corroded anchor bot at projected portion

Corroded anchor bot at projected portion

Corroded anchor bot at projected portion

(OP)
Gentlemen,

I have two questions:

1- As can be seen in the attachment first page (pic) I have this problem.
Corroded part of projected anchor bolt.
Don't know if it needs to be repaired or not? If yes what is a solution.

2- What is the marked portion by the anchor bolt on second page (the two photos)
Thank you

RE: Corroded anchor bot at projected portion

The pdf is too poor an image to tell if the original nut is still present.

Also, what is the remaining effective dia of the anchor bolt. It looks like 1/2 original diameter? 1/4 original strength then? Maybe?

RE: Corroded anchor bot at projected portion

As that is a stiffened base connection, obviously in an industrial facility, the bolts would presumably be in tension with some load conditions, so required. But located inside the flanges like that, it is questionable how much load they were supposed to take. I would want to know the load the bolts need to take before planning any reinforcement, as a solution to inadequate capacity will not be easy.

RE: Corroded anchor bot at projected portion

(OP)
racookpe1978, I am waiting for this info from field. Don't have it yet.

hokie66, I don't have the loads, probably I need to run a full analysis of structure to get the loads unless there is a way around it

Any body knows where I can find a similar problem solved or discussed in a book or ...


Thanks

RE: Corroded anchor bot at projected portion

A typical way to replace compromised anchor bolt is core drill around the existing anchor bolt and remove them. Then replacement anchor bolt is epoxy grouted into the cored hole. Of course you need to know thickness of the slab it is embedded in.

In your photo the anchor bolts project far above the concrete to allow an longer length of the bolt to stretch when the nuts are tightened. This extended stretching length minimizes the chance of the anchor bolt failing in tension.

See this link for an example: http://www.adhesiveservices.com/Report6.pdf

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Corroded anchor bot at projected portion

(OP)
Dear SlideRuleEra,

Thank you so very much for your input, comment and information.
Especially thanks for the link. It was very good.

Sincerely,
SKJ25POL

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources