Cantilever Wall Supported by Concrete on Deck
Does anyone have any (Canadian) design examples of a wall supported by concrete on deck? The wall will be orientated both parallel and perpendicular to the deck flutes. The wall will not be supported at the top and thus will be imparting moment to the concrete on deck at the base of the wall.
My concern is mainly due to bending moment in the concrete on deck when the wall is parallel to the deck flutes.
Great spirits have always encountered violent opposition from mediocre minds - Albert Einstein
RE: Cantilever Wall Supported by Concrete on Deck
BA
Mike McCann, PE, SE (WA)
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
If this is internal, on a well supported span of concrete covered deck, fine. It won't be easy, but you can make it work with through fastening and additional reinforcement in the topping slab. This has been done in a Police station I am aware of... But I don't think it saved any money. It was done not to vary the construction, and was only one isolated location. The rest were CMU boxes sitting on deck pan, all with an open end (ie: Cells).
This way, your vertical loads aren't relying on a thin concrete deck to develop their capacity.
Some more context:
Yes this must be a free standing wall; if it could be supported at the top I would not have a problem.
The concrete on deck is existing 90 mm concrete on 75 mm deck.
The new wall is going to be a glass wall cantilevering out of a supporting U-shaped shoe.
My current design utilizes plates above and below the concrete on deck to engage a larger portion of the concrete on deck and thus minimize local failures.
My original post arose from thoughts regarding if I could simply anchor the wall to the concrete on deck and avoid the plate below. My thinking was that removing the plate below from my design would shrink the failure area in the concrete on deck and reduce the capacity. I am curious to see if anyone else has completed an analysis like this before.
The alternative is providing new beams below the existing concrete on deck to provide positive support at discrete locations along the length of the wall.