I'm reviewing another engineer's fix at the behest of the owner.
While pouring the elevator shaft walls, the inside forwork gave a bit. As a result, the walls were cast about 65 mm thicker than planned for about three upper floors. To get the elevator to fit, the contractor ground the extra 65 mm off of the interior of the walls. In some locations, this exposed or nearly exposed the interior mat of rebar.
The specified fix involved two measures:
1) A Sika mix skim coat has been applied to the interior to cover the bars. The manufacturer's min specified thicknesses is 19 mm. In some places, the installed thickness is as little as 6 mm. Essentially, I consider it to be an exposed rebar condition.
2) Some vertical channels have been bolted to the outside of the shaft, presumably to replace interior rebar that is no longer effective.
So my questions are:
1) From a durability perspective, how big of a deal is exposed rebar on the inside of an elevator shaft if that rebar is no longer being relied upon for strength?
2) How well do we like exterior replacement reinforcing? I've seen this done to reinforce beams and slabs often. I've wondered if bolt hole slip didn't render these solutions ineffective because io the strain required to fully engage the externally applied steel.
Thanks for your help.
KootK
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
While pouring the elevator shaft walls, the inside forwork gave a bit. As a result, the walls were cast about 65 mm thicker than planned for about three upper floors. To get the elevator to fit, the contractor ground the extra 65 mm off of the interior of the walls. In some locations, this exposed or nearly exposed the interior mat of rebar.
The specified fix involved two measures:
1) A Sika mix skim coat has been applied to the interior to cover the bars. The manufacturer's min specified thicknesses is 19 mm. In some places, the installed thickness is as little as 6 mm. Essentially, I consider it to be an exposed rebar condition.
2) Some vertical channels have been bolted to the outside of the shaft, presumably to replace interior rebar that is no longer effective.
So my questions are:
1) From a durability perspective, how big of a deal is exposed rebar on the inside of an elevator shaft if that rebar is no longer being relied upon for strength?
2) How well do we like exterior replacement reinforcing? I've seen this done to reinforce beams and slabs often. I've wondered if bolt hole slip didn't render these solutions ineffective because io the strain required to fully engage the externally applied steel.
Thanks for your help.
KootK