Is there a limit?

Is there a limit?

Is there a limit?

(OP)
Is there a limit to how many reclosers can be coordinated in series?

RE: Is there a limit?

In theory, perhaps not; in practice, absolutely.

RE: Is there a limit?

(OP)
What would govern the limit in practice?

RE: Is there a limit?

To maintain coordination, your current and time dial settings would get a little ridiculous/impractical.

RE: Is there a limit?

(OP)
The setting must allow longer fault durations at the reclosers in the beginning of the feeder?

RE: Is there a limit?

Relatively longer to satisfy necessary CTI, but should not exceed the time as per damage curve of protected device. Consequently, if there are too many, it will be impractical to achieve coordination. But as to the limit, I haven't read any standard and you can install as many as you want but could be impractical at some point.

How many units are you planning to coordinate?

http://www.powerqualityworld.com

RE: Is there a limit?

(OP)
Right now its about 6 units but varies upon contingencies. The number is so high because this is a recloser loop scheme. Basically the feeder is broken up into 250 to 1000 customer chunks. Every segment has a normally closed source recloser and a alternate tie recloser.

RE: Is there a limit?

That's interesting. Anyway, if ever you encounter a coordination problem, I think you can consider using sectionalizers depending on the intended application.

RE: Is there a limit?

(OP)
Have you heard of such being done?

RE: Is there a limit?

Nah.. In our case, it's already difficult to coordinate more than 4 reclosers. And that's where sectionalizers come in.

http://www.powerqualityworld.com

RE: Is there a limit?

(OP)
Looks like some of the reclosers will need a sectionalizing responce built in rather than time over current.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources