I am designing a closed loop cooling system for multiple consumers at varying heights above baseline. The system will include a vented (open top) expansion tank to account for fluid expansion due to temperature differentials. The bottom of the expansion tank will connect to the suction side of the pump. Also several vents will be connected between the top (air side) of the expansion tank and various high points in the system. Is it sufficient to locate the expansion tank simply at the highest point of the system or is there a minimum height that has to be met (calculated) in order to prevent media from coming out the top of the expansion tank vent? Is there a design standard or guideline for design of open expansion tanks that can provide direction? Your comments are appreciated. Thanks.

RE: Open Expansion Tank Location

Highest, highest point.
There is no apparent reason that the bottom of the tank must be connected to pump.

you must get smarter than the software you're using.

RE: Open Expansion Tank Location

(OP)
The expansion tank is connected to the pump suction in order to create a point of zero pressure, or at least near zero pressure.
I thought there would be a requirement for the expansion tank to be a certain distance above the highest point of the system but haven't been able to find this requirement in reference material.. maybe it does not exist.

RE: Open Expansion Tank Location

(OP)
Looks like Mark's Mechanical Engineers Handbook says open expansion tanks should be located at least 3 feet from the highest point radiator or main.

RE: Open Expansion Tank Location

In a closed loop system, all points are connected to pump suction.

you must get smarter than the software you're using.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources