Unbalance delta load connected to star source

Unbalance delta load connected to star source

Unbalance delta load connected to star source

(OP)
Hi,

I want to know the implications of connecting unbalanced delta load to secondary (Star Winding) of transformer.

Thanks.

RE: Unbalance delta load connected to star source

An unbalanced delta load. That means no neutral, so there shouldn't be any current in it.

It depends on the primary winding. If it is a delta winding, then your ampere-turns will be OK. If it is a wye winding - the ampere-turns do not agree so well and you get voltage drops.

Is it a Y/Y or a D/Y transformer?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Unbalance delta load connected to star source

(OP)
Its a D/Y Trafo

RE: Unbalance delta load connected to star source

Shouldn't be a problem then.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Unbalance delta load connected to star source

(OP)
Dear Skogsgurra

Can you suggest some reading material on this topic ?

Thanks.

RE: Unbalance delta load connected to star source

You will have unbalanced line currents on the delta side.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Unbalance delta load connected to star source

Quote:

An unbalanced delta load. That means no neutral, so there shouldn't be any current in it.

Yes, but it's hooked up to a WYE transformer, hence there is a neutral.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Unbalance delta load connected to star source

Is the centre of the star point earthed?

RE: Unbalance delta load connected to star source

(OP)
Yes it is earthed.

RE: Unbalance delta load connected to star source

Sorry to be a bore. But, if there's a wye secondary, and the load is delta. Where can any neutral current flow?

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Unbalance delta load connected to star source

OK, if it is earthed then there is no big deal. If it was floating, then that's a different kettle of fish.

RE: Unbalance delta load connected to star source

Egad, belay all that. I've just realised that the load is delta (thanks, Gunnar - and an abashed grin). Doesn't matter if it is earthed or not.

RE: Unbalance delta load connected to star source

Let me try. There is a neutral point at the transformer wye winding, none at the delta load, and no neutral current involved with this load.

RE: Unbalance delta load connected to star source

@Skogsgurra "If it is a wye winding - the ampere-turns do not agree so well..."
Why wouldn't the amp-turns match in this case?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources