Construction Joint in STM Designed Transfer Beam
(OP)
Please refer to the PDF sketch attached.
A construction joint has been constructed that crosses a major concrete transfer beam that we've designed using strut and tie methods. The joint cannot be relocated to a more favourable position.
For a non-STM designed beam, I would address this issue using shear friction provisions. Additionally, I would count on my flexural tension reinforcement to pull double duty as flexural / shear friction steel. If any additional shear friction reinforcement was required, I'd add it to the beam tension steel per ACI recommendations.
Because the girder under consideration was designed using STM methods, I'm wondering if the procedure described in the previous paragraph is still valid. To be consistent with my STM design, I feel that:
1) I should be able to use the horizontal component of the compression strut crossing the joint as an effective clamping force for shear friction computations.
2) I should concentrate any additional reinforcement required for shear friction over the calculated height of the compression strut.
3) I should calculate the maximum permitted shear stress using the vertically projected area of the compression strut rather than the area of the entire beam.
On the one hand, I feel that my shear friction design should be consistent with my STM design, as described above. On the other hand, I feel that the "right" answer should be the same for both STM and sectional design methods.
Please advise.
KootK
A construction joint has been constructed that crosses a major concrete transfer beam that we've designed using strut and tie methods. The joint cannot be relocated to a more favourable position.
For a non-STM designed beam, I would address this issue using shear friction provisions. Additionally, I would count on my flexural tension reinforcement to pull double duty as flexural / shear friction steel. If any additional shear friction reinforcement was required, I'd add it to the beam tension steel per ACI recommendations.
Because the girder under consideration was designed using STM methods, I'm wondering if the procedure described in the previous paragraph is still valid. To be consistent with my STM design, I feel that:
1) I should be able to use the horizontal component of the compression strut crossing the joint as an effective clamping force for shear friction computations.
2) I should concentrate any additional reinforcement required for shear friction over the calculated height of the compression strut.
3) I should calculate the maximum permitted shear stress using the vertically projected area of the compression strut rather than the area of the entire beam.
On the one hand, I feel that my shear friction design should be consistent with my STM design, as described above. On the other hand, I feel that the "right" answer should be the same for both STM and sectional design methods.
Please advise.
KootK
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.






RE: Construction Joint in STM Designed Transfer Beam
RE: Construction Joint in STM Designed Transfer Beam
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
In repairing that one, I put two rows of four rebar (Reidbar to be specific, but the closest you'd be able to find would be DYWIDAG) and developped them with Hilti Hit HY-150. On the free end I had bar terminators installed.
Effectively both the concrete design manual of connections I used in New Zealand (XXX) and the Hilti International Manual recommended treating this as developed steel crossing the joint. I guess that puts me in the Hokkie66 camp of non-shear friction engineers.
Since you have the ability to put whatever you want in to allow for the cold joint, I would solve this by providing fully lapped tension and compression steel, possibly using face couplers (Lenton if you had to, but DYWIDAG would be best with screw-in formwork style types as a fall back) and then use coil steel to ensure good shear transfer across the joint.
Bear in mind that many, MANY, of these cold joints have been built successfully over the years with just surface roughening to + or - 3/8" and SSD condition at pour. Some steel across the joint is a nice security blanket, but with good workmanship it is not necessary.
RE: Construction Joint in STM Designed Transfer Beam
What you've described is shear friction. I'll just have to cross my fingers that Hokie doesn't see this. Can you supply the title of your NZ connections manual. That sounds like something that I might like to procure.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
You can try to find it online, or just click here: https://duckduckgo.com/l/?kh=-1&uddg=http%3A%2...
*evil smiles* Some really great detailing in there...
RE: Construction Joint in STM Designed Transfer Beam
As best as I understand it, in shear-friction you're calculating the strength you'll get from the amount of shear and area of roughened concrete. I don't buy that. I think you can safely rely upon the Vc and Vs if you do your detailing well, but if you try to go beyond this you're a fool.
I hope Hokkie66 DOES post; I am a huge fan of learning here and he's very much the kind of engineer we can learn alot from...
RE: Construction Joint in STM Designed Transfer Beam
My $0.02. I would distribute the shear friction reinforcement over the entire depth of the section between top and bottom reinf. Wouldn't the compression force have a vertical component at the joint? I would also calculate the max shear stress based on the depth of the section rather than the strut.
RE: Construction Joint in STM Designed Transfer Beam
Interesting issue. I have a few thoughts and some experience in this arena that I'll try to layout logically.
I am a bridge engineer with the Oregon DOT. I have used STM during repair work (bearing replacements) to asses the adequacy of diaphgrams/backwalls for use during jacking operations. I only do this when a section design model shows inadequate capacity. These reinforced concrete beams typically have a couple small bars (top and bottom) crossing the joint between the diapgragm and the girder. I am unsure of whether these were placed monolithically, but in the past I have made use of the entire section capacity for interface shear friction (calculated via AAHSTO LRFD) with success.
If I were in your shoes, with your instincts/concerns, I'd draw a free-body diagram. Split the compression strut forces into vertical and horizontal loads and make use of the normal force (clamping) in my calculations. I don't see how it is any different than a prestressing force. In my gut, I feel that the vertical component of the strut is a true shear force resisted by the entire section. I guess I'd ask myself the question, "What if the strut failed in interface shear?". The answer I see is that the entire section would jump in to help. In a true STM model, you could at least count on the remaining section below the strut to act as a support. This section wouldn't be in compression, but it would still add to the overall capacity (and likely contains your steel).
Just some thoughts. Let me know if I need to clarify anything.
RE: Construction Joint in STM Designed Transfer Beam
@Slick: thanks for your 0.02. This is a poll of sorts to that's perfect. I agree 100% that the compressive strut would have a vertical component at the joint.
@Trouser: how have we not met before? You, my friend, are practically reading my mind. I respectfully disagree with this:
Despite being a native speaker of the King's English, I can't really think of a way to articulate my concern with words. Please refer to the muddled sketch attached to this email. I feel that the strut couldn't "hang" from the sections of concrete highlighted in green without those sections of concrete failing in tension. The only way around this, that I can see, would be to provide some hanger reinforcement beside the cold joint to deliver the shear up to the top of the beam. But then that would essentially be adding an extra tie to the STM model. And I've done that on occasion for exactly this reason. That reason being either paranoia or a lack of fundamental understanding I suppose.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
RE: Construction Joint in STM Designed Transfer Beam
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
Test your GoogleFu:
EVALUATION OF BENT CAPS IN REINFORCED CONCRETE DECK GIRDER BRIDGES, PART 2
FINAL REPORT
ODOT RS 121
Dr. Christopher Higgins, Oregon State University
I believe that you can find this report online for free. The report is quite useful for visualization and application. I’d suggest taking a look at how these beams fail. The report uses common Oregon inventory for the selection of bent caps breaks down the analytics using STM. The study finds that STM is still quite conservative, even with poor column details and poor bent cap longitudinal steel (straight bars – not developed). In essence, we already have suspenders and belts in place…we don’t need to overdesign these sections. More steel could cause as many issues as it fixes (poor placement = bad interface friction). Don't be that kind of engineer. If you're concerned, talk with your inspectors!
Some other thoughts…have you considered addition another truss configuration to the analysis? Re-arranging your truss so that a vertical member is located at the joint could be an alternate way of analyzing this section? This would let you evaluate the joint as another case within the model used for other design elements.
Again, I’d really stress how the compression strut will fail in interface shear. For the interface shear failure to occur within the compression strut, strains would be sufficient to mobilize the entire section. This won’t be an exploding beam and there is still plenty of interface shear friction in your remaining section, outside the compression strut.
Something else that I've noticed, the saltier engineers seem to be comfortable with the fact that past practice shows this is likely of no concern. If it isn't codified, it hasn't caused many issues.
RE: Construction Joint in STM Designed Transfer Beam
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
RE: Construction Joint in STM Designed Transfer Beam
I believe that columns -- all columns -- do in fact have inclined joints. Several actually: 15deg, 30 deg, 60 deg... and at every location along the columns too. Those joints are just monolithic, held together by shear friction (or the atheist equivalent), and perhaps... imaginary.
Why would I bother to say something so fru-fru and bizzare? Imagine me in seated lotus position as I type this. For me, the imaginary shear friction plane idea from the other thread has a very practical application. It allows me to be less conservative when dealing with surprise cold joints. Here's how it goes:
1) Contractor calls me up and proposes / tells me about a unplanned cold joint.
2) I freak out. You put a cold joint WHERE? It's the worst possible location.
3) I remind myself that there was always a slip plane at the proposed cold joint location. The only difference is that it was originally a monolithic shear friction joint and now it will be a roughened shear friction joint.
4) I check the numbers (mu = 1.4 vs 1.0) and, if things work out, I carry on.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
@Trouser: In the interest of full disclosure, I still haven't read your OR DOT document yet.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
We could never know the truth state of stress in any case. Wooten FTW.
RE: Construction Joint in STM Designed Transfer Beam
I can't see your belief that there are inclined planes in columns, except at crush load. Think failure modes of concrete test cylinders.
For struts, I still want bearing normal to the force, not on an incline.
RE: Construction Joint in STM Designed Transfer Beam
To follow a recipe and advocate faith in place of understanding is to turn your back on what being an engineer is all about. Not knowing the true state of stress is only a valid cop out if you're dealing with a ductile system that can redistribute the load to some other capable path. Not so here.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
RE: Construction Joint in STM Designed Transfer Beam
In the context that I've used the term, an "inclined plane" is just an arbitrarily chosen plane of study. It's a stroke of a pen. It is still, however, a plane upon which shear slip must be resisted. And that's the crux of my point. Whether a particular shear slip plane is a physical discontinuity or a hypothetical construct within a monolith, a real mechanism of shear resistance must be present along that plane.
A cold joint on a particular plane just transforms that plane form being a hypothetical construct to being a true physical discontinuity.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
I was just giving CEL a hard time. And you were never on the Christmas card list. I've got other plans for you. My wife and I are planning a trip to Australia in the near future. Itinerary item #89:
89) Find Hokie. Ply with alcohol. Convert to shear friction lover.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Construction Joint in STM Designed Transfer Beam
And Hokkie said it perfectly.