Slab cracking matches WWM

Slab cracking matches WWM

Slab cracking matches WWM

(OP)
Hey folks. Has anyone seen this before? Any idea of potential causes?
2nd floor slab, 2.5" NW concrete topping over 9/16" deck over bar joists at 24" max.
Exhibits through much of the slab (to lesser extent in some areas).
Photos show the mesh chaired, tied and in the proper location...of course those could have been selectively chosen.
Some portions poured in sun others in shade, fair weather, temps in low to mid 80's.
Thanks

RE: Slab cracking matches WWM

So much for crack prevention.

perhaps the chairs were too tall? or the concrete wasn't poured the whole thickness.

RE: Slab cracking matches WWM

That looks like plastic settlement cracking to me: Link.

The slab system is quite thin. What was the design cover on the WWM?

The greatest trick that bond stress ever pulled was convincing the world it didn't exist.

RE: Slab cracking matches WWM

(OP)
KootK: Thanks for the link. 3/4" cover minimum. We've spec'd this type of slab hundreds of times without trouble. I wonder if vibration would prevent plastic settlement? The mix designs were fine, perhaps they added a boat-load of water.

RE: Slab cracking matches WWM

I have seen things like that when the reinf to too close to the top.

RE: Slab cracking matches WWM

They didn't drop the mesh into wet concrete? I've seen people do that before.

RE: Slab cracking matches WWM

KootK is correct. Cracking which mirrors the reinforcement is invariably plastic settlement cracking. But in such a thin slab, the remedy of revibration was not available. Perhaps your contractor was too diligent in keeping the top cover. It would be better to put the mesh in the centre of the slab.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources