whats the cable size required to connect between 33/132 kV transformer and 132/400 kV substation for 130 MW,length = 500 meter ?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Cable size
http://www.tfcable.com/wp-content/uploads/2011/06/...
1*400 mm^2 copper conductor. You have to check your conditions if it is underground [earth thermal resistance, distances between cables or ducts, depth and other].It will be better if you will consult a specialist.
An overhead transmission line it will be preferable [it is cheaper!].
RE: Cable size
If you are in AIS, you can use an OHTL, will be about 8-10 times cheaper than a cable.
RE: Cable size
Size should be 2 nos. of 400 sq.mm copper conductor (considering cable derating also) and based on 130 MW (710 Amps), length 500 M.