I am currently trying to determine the adequacy of an existing vent in a tank for a pressure relief scenario. Is there a particular equation or calculation to verify what size vent is needed?
I have looked through API 2000, NFPA 30 and Crane TP 410 (the most difficult to interpret) and thus far have come up with sizing tables given the wetted area and flow rate into the tank. What I want to know is where those vent size numbers come from for a given capacity.
Thank you in advance for your help.
I have looked through API 2000, NFPA 30 and Crane TP 410 (the most difficult to interpret) and thus far have come up with sizing tables given the wetted area and flow rate into the tank. What I want to know is where those vent size numbers come from for a given capacity.
Thank you in advance for your help.





RE: Vent size on atmospheric tanks
The vent sizes per wetted area are determined based on the allowable pressure or vacuum in the tank, the inbreathing or outbreathing requirement based on the flow rates out of and into the tank, thermal effects from tank contents evaporating, and emergency conditions such as a fire.