I have a customer that wants to move the computers out of a room and people in keeping the fm200 system in place. i seem to recall that these rooms are for equipment only. anyone have any idea if the code restricts occupancy of rooms protected by fm200 systems?
Thanks in advance
Thanks in advance





RE: OCCUPYING A ROOM WITH fm200 SYSTEM
Does this room presently have a fire sprinkler system?
The idea is if the system dumps, people leave the room.
Yes they are used in occupied areas, but not normally an office setting.
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
What they are proposing is perfectly compliant with NFPA 2001 and most likely your fire code.
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
There is yearly upkeep of the system involved
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
Anyway their call
RE: OCCUPYING A ROOM WITH fm200 SYSTEM
the usual
$ . they are going to be moving out in the next little while anyway.
Have them disconnect the bottles, that will not cost a lot. Heck they may even get $$$ for the gas in the bottles. You have the preaction sprinkler system so you have the required protection.