Hi all,
I am getting a lot of complaints about recently commissioned Centralised AHU system serving an open plan office.
There are a number of wall temperature sensors in the area and they all read the desired values (between 20.3 C & 21.8 C to a set point of 21 C). The supply air temperature is 15 C but even at the supply air temperature of 18 C the complaints were still coming through.
The ceiling in the office steps up by 1m half way through and only the people in the area with the higher ceiling complained.
As the AHU operates in cooling mode I would expect the people under the lower ceiling to complain more– if there are any problems. What’s happening is totally opposite.
The velocities through the ceiling diffusers are reasonable low ( less than 2.5) but in any case are the same across the whole office.
Can the 'coanda' effect speed the air up along the higher walls causing more draught?
The humidity is not controlled nor there is a need for that but it’s generally high.
Has anybody got similar experience?
Regards,

RE: Cold air complaints

Office spaces are tricky, especially open ones. My first thought is the thermostat locations and installation. Are they controllable? If they are on an exterior wall is there insulation between the wall and sensor? Are the thermostats in direct sunlight? Without further knowledge of the design and layout these are my first thoughts.

Also, 21.8 seems to be low per ASHRAE. ASHRAE recommends about 23.9C. Have they tried increasing the space temperature setpoint?

RE: Cold air complaints

The coanda effect will definetely cause dumping in the high ceiling area.

RE: Cold air complaints

You will never make everyone happy about temperature in an open office, where you have women in skirts, men in suits and ties, sunshine through different windows at different times, and differences in personal preferences.
Accutherm thermostatically controlled diffusers may help, but probably not.

RE: Cold air complaints

20 - 21 C in an office sounds a bit cold. 22-24 C range usually keeps most people happy.

RE: Cold air complaints

office temperature should be 26 C. 24 C is ok only if there is determined corporate practice that everyone wears long sleeves.

i am talking about thermostat setting. if you count variations of 1-2 C inevitable for open spaces, your will find that with your 20 C measured it could be found down to 18 C and some spots, and everyone will complain in such circumstances.

raising temperature setting should be first solution to attempt with. if someone would complain for feeling too hot afterwards, you should check local heat sources. you would not want freezer atmosphere in open office only because two seats are too close to concentrated location of hubs/copiers etc.

this question seemingly has to be tied to office space organisation.

RE: Cold air complaints

(OP)
Thank you all. I will ramp the set point temperature and see how it goes. I went by CIBSE recommendations of 21 C ( +- 2 degC).
The hunidity around here is ususally high which doesn't help either.

Regards

RE: Cold air complaints

Perhaps I should not say this here.
But one thing that has been useful with complaints from people in an otherwise well balanced office.
Is a dummy thermostat closest to the loudest complainants.
B.E.

You are judged not by what you know, but by what you can do.

RE: Cold air complaints

Is the complaint actually temperature or that they feel cold air blowing on them? Perhaps a diffuser relocation would end the complaints.

RE: Cold air complaints

“The velocities through the ceiling diffusers are reasonable low (less than 2.5)” Less than 2.5 What? Furlongs per Fortnight? Use units.

This sounds like a classic case of over sized DX.

RE: Cold air complaints

Tell people who complain about the cold air to wear sweaters

RE: Cold air complaints

And bras that can conceal perky nips...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources