Hello experts,
I am working on a project where ................
Two air-handling units located in one mechanical room serve two separate fire-zone. Return air is ducted. Mechanical room has tight space.

If I delete return-air ductwork inside mechanical room and make it as common plenum with fire-dampers at the mechanical room wall openings, does it comply with the code?

One of my friend argued that it does not comply with the code but he could not give me clear explaination

Please advise

RE: Mechanical Room

Have you checked the code yourself? Which code?

RE: Mechanical Room

What code you are talking about, there are tons of codes.
What kind of building is it, residential, commercial ....etc.
You have all duct return installed and you are worry about a piece of duct between mechanical room wall and air handler.

RE: Mechanical Room

(OP)
sorry, I forgot to mention,,,,,,,,,,,, We are using International Mechanical Code (IMC)

RE: Mechanical Room

The answer is no, your friend is correct. Plenum is limited to one fire zone. Refer to 602.1.

RE: Mechanical Room

What about two commercial suites separated by a fire separation served by on air handler

RE: Mechanical Room

You can have multiple zones, multiple floors and multiple occupancies off the same air handler, and even combine NFPA 90A and NFPA 92 on the same AHU for all those floors and zones. Looks really messy on a pneumatic control system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources