Running 3-phase motor on single phase
How many mfds are necessary to run a 5hp 3 phase 415 volt motor on 240 volt single phase?
RE: Running 3-phase motor on single phase
http://www.boost-energy.com/
You have to change the motor voltage,usually by reconnecting in delta.
Take into account,starting torque and load torque.
Run capacitors are slow starting on their own.
Start capacitors need a means of disconnection.
Zanoter has the right idea,use a purpose designed inverter.
To answer the question (the way it is put): You can make the motor turn with just about any impedance that introduces a phase shift with regard to the inductive motor winding, you don't really need a capacitor. I once used an overhead projector just to make the point. So, making it run is not a problem.
The problem is to make it run efficiently with a load. And there, the 415 V motor will have a problem with 240 V. And you will never be able to get the rated power out of it. Not even if you reconnect for the existing voltage, which is not always possible.
Use a VFD. As has already been recommended. But you still need to adapt voltage. There are no VFDs that can produce three-phase 460 V out of single-phase 240 V.
Gunnar Englund
www.gke.org
If the motor cannot be reconfigured for 230V 3 phase, then regardless of which way you go, you must also then use a transformer to get your single phase voltage to 415V prior to trying to accomplish the phase conversion. All of this typically makes it simpler and easier to just go out and find a 5HP 230V single phase motor to be quite frank.
"Will work for (the memory of) salami"
The capacitor value to make it start, assuming all the other issues work for you, is 67mfd/kW. So if you dont know, to get kW from HP take the HP * .746 (there are 746 watts per HP).
Thank you all for the responses. This is my first time on this forum and I love the response you have given.
For the record, I am an ex-electrical engineer in Australia and have managed 97 years without electrocuting myself so far.
My son-in-law has got me started on this forum and is typing this for me. My future messages may need allowances made for my keyboard skills, or lack thereof.
Henry
Gunnar Englund
www.gke.org
Also, what is connecton of three phase motor, star or delta?
http://winding.wix.com/design
Bill
"Why not the best?"
Jimmy Carter
Apprenticed aged year 16
Winding armatures aged 14
Birthday 30/4/2017
To everyone else
Job 1. 3 hp vacuum pump 2800RPM star now delta
Capacitors fitted one 60 three 30s MFDs
Starts no problem. Runs enough revs. Motor gets fairly warm so using an external fan.
Job 2. Not started.
1500RPM compressor load will fit 2hp single phase to assist 5hp.
Thank you for the welcome Bill
Henry
I wasn't born yesterday nor in two years time!
That birthdate should have read 1917.
Henry
Did you reach that impressive age thanks to lots of safety measures (Hard Hat, Goggles, Rubber Gloves, Ear Protection, Steel Tipped Shoes, Breathing Mask, Arc Protection, Shrouded Banana Plugs, Fused Test Leads) and all such stuff?
Or were you just knowing what you were doing?
Gunnar Englund
www.gke.org
An old electrician/engineer once told me;
"I never wanted to be the smartest electrician. I always wanted to be the oldest electrician!"
You have probably won that title, Henry.
Bill
"Why not the best?"
Jimmy Carter
We had a slight technical hitch.......Henry accidentally started a new thread instead of replying on this one. So this is the son-in-law again, giving him a bit of a hand. He always excuses his errors by saying "I'm just a boy - still learning".
I've copied his reply from the new thread and it is below, with a few corrections (Henry makes no claims to being a keyboard whiz). I don't know if I can delete the additional thread but I'll try after finishing this....
This is Henry. I connected the 3hp star circuit to delta and put 200 mfds in one phase and started the motor. The motor ran up to full speed and I removed 150 mfds leaving 5o mfds. The motor stayed on full speed and did not get hot after running for 2 hours. I am so pleased for the help from the forum.
Henry the Eighth
Curt Wilson
As was already said, VFDs are cheap these days.
From 3 phase to single phase you most use an Steinmetz connection, the capacitor value could be calculated by the following:
C = 36*P* [(220/U) Squared] * 50/f where: C is microFarads, P is motor power output in kW, U is the single phase voltage and f is frequency in Hertz.
Taking account data provided your capacitor calculation is 112.6 micro Farads (I have use 230 V and 50 Hz) it´s a big capacitor, maybe you will need an arrangment of two 60 micro farads capacitors.
You can connect the motor in star or delta and it depends of your power source available, if you use 230 or 240 volts choose delta connection. ( if the original three phase motor connection is star for 415 Volts) and you will need an AC capacitor at least for 460 V.
For connection please take a look of attached pictures.
My experience sayd that this calculation is your starting point, so is possible that you need to deal with trial and error in order find the right capacitor (or arrangment), because you need watch the motor currents balance.
This connection has several drawbacks due to current umbalance and , 1/3 of power output loose.
For small motors the best alternative is use an inverter to perform this operation, there are several inverters availables in the trade.
Also could be good that you can take a look of this link http://www.serd.ait.ac.th/icue2011/cd/papers/S3/S%...
Hope this can help you.
Best Regards
Carlos
Welcome to the forum. Lots to learn and nice people. I hope to emulate you. Well done. My dad was born in 1919. Survived WW2 and then was murdered in Bulawayo, Zimbabwe. It is always a joy to have young people introduce others to all the great stuff. Keep going.