CT SIZING FOR PRIMARY PROTECTION RELAY

CT SIZING FOR PRIMARY PROTECTION RELAY

CT SIZING FOR PRIMARY PROTECTION RELAY

(OP)
Lets assume that we have a 10,000 kVA 138 kV to 12.47 kV transformer with a primary FLA of 41.8 A.

The short-circuit available at the secondary side of the transformer is 5.76 kA which referred to the primary side is 520 A.

Assuming this CT feeds a typical electromechanical 50/51 relay (CO 8) about 100 feet away from the CT, would you choose a 50/5 CT for this primary relay?

Would you consider a C400 accuracy class for this application?

Are there any commercially available CT products (50/5 C400 or C800) readily available and of a reasonable size to install in an average sized equipment?

Thanks.

RE: CT SIZING FOR PRIMARY PROTECTION RELAY

Yes, I'd likely pick a 50:5 CT but not necessarily a C400. The class depends on how it's applied. For this application the CT burden is mostly the lead length.

RE: CT SIZING FOR PRIMARY PROTECTION RELAY

It sounds like you're going to need a free-standing CT and not an internal bushing CT, due to the low ratio.

At 15 kV, C200 is the commonly available protection class for free-standing CTs. It is possible to get a 50:5A with a C400 rating, but it would be a good deal more expensive, larger, by special order. You would have to confirm for yourself, but with only 200 feet round-trip of leads, I'm guessing a C200 would work fine.

As for physical size, if you go with a free-standing CT, where would you put it? Easiest would be an outdoor CT mounted next/near to the transformer.

RE: CT SIZING FOR PRIMARY PROTECTION RELAY

Does the relay protect the primary side of the transformer also?
With such a low ratio CT you need to check if the CT will saturate on a primary fault.

RE: CT SIZING FOR PRIMARY PROTECTION RELAY

Are looking for a high side bushing CT or slipover CT? A standalone 138 kV CT is pretty expensive.

Our protection group usually specs much higher ratio CT's on the high side of all of our similarly sized substation transformers, but I am not quite sure why. Perhaps they future proof for upgrades to transformer differential protection. Perhaps it has to do with possible slow operation of overcurrent relays and high transient voltages in the case of severe saturation as described in these papers:

https://www.google.com/url?sa=t&rct=j&q=&a...

https://www.wecc.biz/library/Documentation%20Categ...

RE: CT SIZING FOR PRIMARY PROTECTION RELAY

If the relay is not close to the CT's it's sometimes good to use /1A on secondary, it will allow you to save some VA in the wiring (RI²) most of the protective relays accept /1 or /5A.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources