STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

(OP)
How to determine the static pressure requirement of an EXHAUST FAN serving a Generator room that is directly installed above the ceiling without duct knowing its capacity?

I know that for a non-ducted exhaust system, usually the SP ranges between .05" to .20" and exhaust system for generator should be designed to maintain a slight positive or negative pressure in the room, depending on the application. Since the generator is in a separate room 20 meters away from the hospital, I chose to maintain a positive pressure inside the engine room so I'll need a static pressure less than .2" .

How to compute for the exact value of static pressure that I need for choosing a exhaust fan? By the way I already have the capacity that I needed, only the SP is unknown.

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

You will have to calculate the static pressure drops in the air paths at a given velocity/cfm.

SMACNA or ASHRAE volumes will list pressure drops

You can find the air paths with smoke.

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

how will you maintain positive pressure?

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

Will your fan have a louver or any other accessories? I would call up a fan representative and ask for a recommendation. Otherwise for a wall exhaust fan typically I would specify 1/8" static. Good luck.

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

Maybe I'm missing something but where is your generator getting its combustion air from?? Unless there is a direct feed, this will make a mockery of your HVAC cal;culations.

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

usually generator rooms are naturally ventilated by using louvered doors / windows.

RE: STATIC PRESSURE FOR A NON-DUCTED EXHAUST FAN

If the generator motor cooling system intakes air from the outside wall with a greater CFM than the wall exhaust fan CFM and any fugitive CFM thru cracks , than you should have a slight positive pressure within the mechanical room. I would not bother calculating, instead I would use the specifications of the manufacturers the motor generator set and match the exhaust fan CFM taking into account any fugitive CFM as an estimate; then install a manometer reading the differential pressure between the outside and the inside of the mechanical room to fine tune. You can make your own manometer with Tygon tubing and colored water to fine tune your work.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources