Ampacity in cable 3kV dc networks

Ampacity in cable 3kV dc networks

Ampacity in cable 3kV dc networks

(OP)
I am looking about ampacity in cable 3kV dc networks, especially rail power systems. In particular about cable trenches with many cables.

RE: Ampacity in cable 3kV dc networks

See [for instance]:
http://www.nexans.com/Poland/2007/CatalogueRolling...
If you know how the cable is build [e.g.-conductor: copper or aluminum, cross section area [sqr.mm] class of stranding: class 5, compressed or compacted-insulation material and thickness [EPR, Silicon, 3.4 mm], screened, jacketed (EPR 2-3 mm) or else, you may calculate the ampacity according to IEC 60287-1-1 and 2-1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources