Single point ground on a ct circuit
After much on the job discussion, what is the primary reason to have just a single point ground on a CT circuit?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: Single point ground on a ct circuit
Steadfast rule for secondary grounds on VT and CT circuit is the secondary circuit must have a ground reference and it should only be grounded at one point.
An even more serious issue is related to scottf's post. In the event of a major system fault, there may be high ground fault currents that may cause voltage gradients. A voltage gradient between multiple ground points of a protection circuit may cause unintended results such as a failure to trip or a false trip. A voltage gradient between multiple ground points may cause unintended currents in CT metering or protection circuits.
Bill
"Why not the best?"
Jimmy Carter
Ground faults on secondary wiring are possible. When there is a ground fault on any of the two wires then both wires are grounded
and there is no open circuit in the secondary circuit.