Point Load on Metal deck w/ concrete

Point Load on Metal deck w/ concrete

Point Load on Metal deck w/ concrete

(OP)
Hello all,

So I have a point load on a metal deck with concerete. I will definately check punching shear but I wanted to check if bending was ok. I have attached a calculation showing what I did to find the bending capacity. Let me know if you think this makes sense, I used a 12" strip. Also, if yoy guys have other methods that would help to.

JO

RE: Point Load on Metal deck w/ concrete

Canam has a number of design examples on their website - including some for concentrated loads.
I've saved the printouts so I don't have the website, but it should be quick to find. I'd follow their procedure.

RE: Point Load on Metal deck w/ concrete

You can use the allowable PSF loads from the deck catalog to back-calculate moment and shear capacity of the deck span. Then compare the moment and shear capacity to the demand from the concentrated load.

RE: Point Load on Metal deck w/ concrete

(OP)
ONCE20036/CANPRO,

In CANAM phiMno is given in their steel deck catalog. I am using VERCO, if I dig around I can probably find something near what I am using in CANPRO I guess.

Steellion,

I like that idea.

JO

RE: Point Load on Metal deck w/ concrete

The only thing steelion's method doesn't take into account is localized web crippling.

RE: Point Load on Metal deck w/ concrete

(OP)
jayrod12,

I think if I check only the 3 1/4" for punching shear, that will eliminate any possibility of web crippling on the deck?

JO

RE: Point Load on Metal deck w/ concrete

Probably, and I also forgot you mentioned there is concrete which significantly reduces the chance of any web crippling

RE: Point Load on Metal deck w/ concrete

(OP)
I actually compared what moment capacity Canam gives you with my calc and it is really close :)

RE: Point Load on Metal deck w/ concrete

I just worked on something similar. In its catalog Verco recommends checking the moment and shear capacity based on the allowable uniform loads. Calculate capacities based on a simple span beam (they assume concrete will crack over supports since it is in tension). Note that the moment capacity and shear capacity are flat lines (eg wl^2/8 is the moment capacity anywhere along the span and wl/2 is the shear capacity anywhere along the span)

RE: Point Load on Metal deck w/ concrete

(OP)
SEARUN,

Where in the VERCO catalog do they recommend that? I would like to see it for reference.

JO

RE: Point Load on Metal deck w/ concrete

Joe,

See page 7 in the Verco Steel Floor Deck. I talked with the Verco engineer about the capacity (flat line). Makes sense- similar to wide flange beam you have the same moment capacity and shear capacity any point along the beam assuming everything is laterally braced, etc.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources