Envirotemp FR3 Fluid for Retrofills

Envirotemp FR3 Fluid for Retrofills

Envirotemp FR3 Fluid for Retrofills

(OP)
Has anyone used FR3 to retro-fill an existing transformer previously filled with mineral oil?

Based on the articles I've read, it will increase the lifespan of the paper and allow for heavier loading. It will also have environmental and insurance benefits.

What are the drawbacks of using FR3? What should I expect to pay per gallon?

Thanks

RE: Envirotemp FR3 Fluid for Retrofills

I dont have personal experience but know a little on the subject. Retrofilling shall be limited to a voltage class max of 33 kV. Cost per unit volume 2 times of mineral oil in US and 3-4 times in other places.
Drawback is quicker oxidation and hence use is limited with sealed construction or conservator with atmoseal(air bag)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources