Foundation Overturning Reduction in ASCE 7
For those who regularly use ASCE 7 in their practice, do you typically take advantage of the 25% reduction in foundation overturning permitted by ASCE 7-10 section 12.13.4? The same provision was included in earlier editions of ASCE 7 as well. My suspicion is that this provision is not widely employed in practice. As I read it, the provision applies strictly to overturning (not sliding) and only applies to foundation members. Of course, you have to meet the limitations set forth in ASCE 7 as well (use of the Equivalent Lateral Force procedure and the structure in question cannot be an inverted pendulum or cantilevered column structure). Since the vertical distribution of seismic forces in the Equivalent Lateral Force procedure is based on the first mode of vibration and that distribution overestimates the overturning force, it makes sense that a reduction in overturning is permitted.
RE: Foundation Overturning Reduction in ASCE 7
Mike McCann, PE, SE (WA)
C12.13.4 Reduction of Foundation Overturning. Since the vertical distribution of forces prescribed for use with the
equivalent lateral force procedure is intended to envelope story shears, overturning moments are exaggerated. (See
Section C12.13.3.) Such moments will be lower where multiple modes respond, so a 25 percent reduction is permitted for
design (strength and stability) of the foundation using this procedure. This reduction is not permitted for inverted pendulum
or cantilevered column type structures, which typically have a single mode of response.
Since the modal response spectrum analysis procedure more accurately reflects the actual distribution of shears and
overturning moments, the permitted reduction is only 10 percent.
I have utilized it occasionally, but I can't think of a time where I have invoked it up-front in design.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.