Faults: Wye Wye versus Delta Wye
I am working on a project which called for a 1500 KVA delta-wye transformer (25 kV to 480V). Somehow we ended up with a wye-wye. Assuming the transformer is the same size and impedance, would the change from delta-wye to wye-wye have any detrimental effects on the fault current? Is there any reason to re-do the short circuit and arc flash studies?
EE
EE
RE: Faults: Wye Wye versus Delta Wye
Gunnar Englund
www.gke.org
But you may want to review your ground fault relaying.
Gunnar Englund
www.gke.org
Thanks again
Bill
"Why not the best?"
Jimmy Carter
EE
When you say that ETAP calculates min and max faults, if it is based on IEE1584 (most likely) it will be calculating 3 phase fault currents and arcing currents. IEEE1584 recommends calculating trip times at 85% arcing current (for LV systems) as well as 100% to see which scenario gives the highest incident energy, but both are 3 phase values. 85% arcing current results in longer trip times. I am not familiar with ETAP, but SKM PTW calculates the incident energy for both cases and reports the worst case, and I suspect that ETAP does the same.