Hi
Can you tell me for a 1500kVA Distribution transformer how much be Total connected load (TCL) and Maximum Demand (M D).
Regards,
Sarath Kurian
Can you tell me for a 1500kVA Distribution transformer how much be Total connected load (TCL) and Maximum Demand (M D).
Regards,
Sarath Kurian






RE: TCL & M D OF A TRANSFORMER
For a utility owned transformer the maximum demand may depend on the duration of the overload and the maximum allowable voltage dip. Loading above 100% leads to poorer voltage regulation and reduced transformer life.
If the transformer is subject to electrical codes then some codes require that the continuously connected load may not exceed 100% of the transformer rating and the maximum demand may not exceed 100% of the transformer rating. Under some conditions the maximums may be 80% of the ratings.
In North America most customer owned transformers are subject to the electrical codes.