Earthing power loss
Earthing power loss
In any power system, the earth fault current goes to several kiloamperes and earthing resistance of 0.5 ohm is quiet common at a substation.
if that is the case, a circulating current between source and fault of say 10 kA and a resistance of 0.5 + 0.5 = 1 ohm leads to a power loss of about 100 MW! (I^2R)
Faults can last for up to 2 seconds and a reasonable power is dissipated, the question is :
where does this huge amount of power go? and if this is the case, the fault power is so high to cause generator rotor angle to stall (What happens is usually the opposite!)
I believe something is wrong with my understanding, any clue?
RE: Earthing power loss
A high magnitude fault may result in an instantaneous trip.
Bill
"Why not the best?"
Jimmy Carter
The fault energy is wasted as I2R losses in the path of the fault current.
Less ambiguous and such calculations will give true power wasted in the fault, not VA, KVA or MVA.
Bill
"Why not the best?"
Jimmy Carter
Also, most power systems of any magnitude do not cause very large currents during a line-ground fault. The realy heavy currents flow during a line-line fault. And then, the path resistance is not even close to 1 ohm. Current is limited by generator reactance, not by the resistance.
Gunnar Englund
www.gke.org
Our utility has begun responding to the increasing amount of distributed generation on our low-tension systems by employing load encroachment relays, which use feeder power factor to discriminate between faults and high loadings based on the notably more inductive nature of fault current.
As for self-excited generators suffering voltage collapse during faults, this is part of a continuum where slow-acting automatic voltage regulators [AVRs] are poorer than quick-acting AVRs, which are poorer than those with field-forcing and/or "transient-stability excitation control."
In this vein, similarly to how aircraft have a 'minimum equipment list' detailing just how much stuff in a given plane can be broken before it's no longer permitted to fly, IESOs have rules stating that no more than a certain number of generators within a given area [as based on system studies] can remain in service with their AVRs on manual, or with resistor field control, before the system fault response characteristic is adversely affected. Since loss of generation is loss of revenue, overtime has routinely been approved to have AVRs repaired overnight so the unit will be available again during the following day's higher primary demand period.
CR