Deflection Criteria for a 36"x36" Marble tile floor...

Deflection Criteria for a 36"x36" Marble tile floor...

Deflection Criteria for a 36"x36" Marble tile floor...

(OP)
Marble tiles will be 36x36 (1.25" thick on a 1.5" mud set)

Using L/600 for the total deflection criteria.

Never worked with tiles that big. Anyone have experience working with this large a tile?

Thanks.

RE: Deflection Criteria for a 36"x36" Marble tile floor...

Deflection criteria sounds ok.

Make sure Architect uses cleavage(slip)membrane between structure and tile.

RE: Deflection Criteria for a 36"x36" Marble tile floor...

We had a stone tile system that required very tight slab-on-grade deflection and curling criteria. We ended up using a unique mix with no control joints (and some reinforcement) to minimize curling and it apparently worked pretty well.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Deflection Criteria for a 36"x36" Marble tile floor...

According to one of Boise Cascade's Technical Bulletins the Marble Institute of America recommends L/720 or <7/32". I haven't independently confirmed if this is true.

RE: Deflection Criteria for a 36"x36" Marble tile floor...

(OP)
Thanks you for the tips. I am going with the L/720. My span is only 14' so I'm not too worried.

RE: Deflection Criteria for a 36"x36" Marble tile floor...

Will want to make sure flatness/levelness is specified as needed as well. Architects should be doing this but often gets shoved back on to structural engineer or, worse, ignored. Commentary to ACI 117 has some good guidelines as to how flat you need to be for various uses.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources