Pre-Engineered metal buildings with Interior Gypsum Walls

Pre-Engineered metal buildings with Interior Gypsum Walls

Pre-Engineered metal buildings with Interior Gypsum Walls

(OP)
I am at a bit of an impasse. I have a design/build project in which the general contractor wants to use a pre-engineered metal building as the frame and walls of a single story office. The architect (my client) has shown the use of gypsum wall board over metal studs which are supported by the building girts. I have been contracted to design the foundations only, but when seeing the detail posed the question as to if deflection had been considered. During a conference call today, I discovered that the wall girts are designed with a wind load deflection of L/90. Obviously this far exceeds what the gypsum can be subjected to without cracking. Have any of you run into this before? I am thinking of suggesting wall studs that span from top of stem wall to a beam (designed by me) meeting the wall board deflection criteria. The studs would be used to support the girts which are still needed due to the siding.

Does anyone have a better idea?

RE: Pre-Engineered metal buildings with Interior Gypsum Walls

Isn't sheetrock ok for L/120? Did they take a 30% reduction in wind pressure when calculating L/90? If not, you would squeak by. (my guess is that they did as they want to use the least material possible)
Gotta love metal building specifiers!

RE: Pre-Engineered metal buildings with Interior Gypsum Walls

Ask the architect if he wants his client's interior walls to breath every time the wind blows? Move the interior walls inboard a bit more, anchor well at the floor and attach the walls at the top only using a diagonal strut.

RE: Pre-Engineered metal buildings with Interior Gypsum Walls

I've never designed them, but I've built out quite a few interiors of PEMBs. I've never seen the interior walls connected to the structure.
The interior walls are stand alone and braced above the drop ceiling. Even fire walls are only connected to the beams or columns, not the girts.

RE: Pre-Engineered metal buildings with Interior Gypsum Walls

Do not span the studs vertically. The wall sheeting will not be properly supported if you do so since the ribs of the sheeting run vertically. Either increase the size of the girts, put the walls inboard of the girts, or forget the sheetrock.

Mike McCann, PE, SE (WA)


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources