change from GRE pipe to HDPE pipe as chilled water piping

change from GRE pipe to HDPE pipe as chilled water piping

change from GRE pipe to HDPE pipe as chilled water piping

(OP)
Gents,
I have been asked to change from GRE piping to DHPE piping for our underground chilled water supply system.
The Existing GRE has worked very well and I do not want to change. But others think different about this new part of underground chilled water piping.
What is your experience. Change to HDPE or keep GRE.

RE: change from GRE pipe to HDPE pipe as chilled water piping

I assume the "others" determined the GRE is deteriorated and needs to be replaced? I assume if it was in good condition, there would not be talk about replacing?

RE: change from GRE pipe to HDPE pipe as chilled water piping

(OP)
No, we have an existing system that is made of GRE pipe. We are now getting a new system where our contractor states that taking HDPE is a better choice than GRE.

RE: change from GRE pipe to HDPE pipe as chilled water piping

Better choice for the contractor's profit.

RE: change from GRE pipe to HDPE pipe as chilled water piping

Unreinforced plastic pipe will have a significantly greater CTE(coefficient of thermal expansion). This may or may not be a problem where temperature cycles.

RE: change from GRE pipe to HDPE pipe as chilled water piping

I worked in an office where they used HDPE for the entire geothermal system. Seems to work fine. My only issue with HDPE is the sizing method.

HDPE pipe utilizes the iron pipe method. While this may not be too much of an issue with smaller pipe, it can come back to haunt you later. See this Link for information regarding pipe size and wall thicknesses. I believe DR9 is common for geo systems, but each size has it's own pressure rating so be careful with use in a chiller system.

Don't for one minute think the pipe sizes will be a 1 for 1 swap. A project I was a part of called for an 8" HDPE pipe from the geo field to the building. The pipe was installed and when revisited to run the calcs, the head requirement on the pump was much greater. To achieve the design intent of the system and 10" HDPE pipe would need to be installed, to get the 8" internal diameter. The pump went from a vertical inline to a double suction (the 8" HDPE pipe was rather long).

I suggest revisiting the calcs before allowing this change. It may not be cost effective in the long run.

RE: change from GRE pipe to HDPE pipe as chilled water piping

Just a question - if lines are to be insulated, and hdpe is more outwardly permeable to water than alternatives, what will be effect on insulation?

RE: change from GRE pipe to HDPE pipe as chilled water piping

I would like to ask regarding the piping in FCU/HVAC, is it possible to install black steel pipe or copper pipe in the piping of FCU/HVAC and what standard I will use to justify that both can be use.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources