neutral connection of CT
|
neutral connection of CTneutral connection of CT(OP)
usually only one point in the neutral connection of a CT is earthed .why is it so?
thanx Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: neutral connection of CT
Earthing the neutral at more than one point can lead to circulating currents in the neutral wire. These currents can affect the CT secondary circuit (through induced currents) and cause maloperation of the respective protective relays.
RE: neutral connection of CT
RE: neutral connection of CT
"...so that the station ground bus itself will never serve to complete any part of the instrument transformer secondary circuit."
RE: neutral connection of CT