First, I'm a mechanical engineering student, so I'm not familiar with the US building codes pertaining to this issue. This is also not coursework, but curiosity.
I have encountered a staircase in an industrial setting that is anchored at one end to diamondplate only. One side of the staircase end rests directly on diamondplate (is welded), several inches from the nearest beam connection. The other side of the same staircase end rests on air, next to diamondplate, with a 3" weld between them that would be subjected to shearing through the weld thickness. There are flanges on the diamondplate but no beam supporting it at the staircase.
My gut feeling is that a metal staircase should be connected beam-to-beam at both ends, and that diamondplate should not be used as a primary structural support. However, I don't know where to look to verify this. I found guidelines on the construction of the actual staircase but not regulations on how it would be attached.
Can someone direct me to the appropriate resource, or give me some guidance backed by more experience than I have?
I have encountered a staircase in an industrial setting that is anchored at one end to diamondplate only. One side of the staircase end rests directly on diamondplate (is welded), several inches from the nearest beam connection. The other side of the same staircase end rests on air, next to diamondplate, with a 3" weld between them that would be subjected to shearing through the weld thickness. There are flanges on the diamondplate but no beam supporting it at the staircase.
My gut feeling is that a metal staircase should be connected beam-to-beam at both ends, and that diamondplate should not be used as a primary structural support. However, I don't know where to look to verify this. I found guidelines on the construction of the actual staircase but not regulations on how it would be attached.
Can someone direct me to the appropriate resource, or give me some guidance backed by more experience than I have?






RE: Metal staircase attachment - no beam
You're not likely to find a regulation specifically prohibiting the crappy connection details that you've encountered. And part of the reason for that is that, under the right circumstances, one could support a stair case from connections to the floor plate alone. It would be weird, and would require some calculation to justify it, but it could be done.
An excellent reference on stairs can be downloaded for free here: Link. It will tell you a good deal about how stairs are typically detailed but it won't supply a prohibition on the kind of connection details that you're seeing.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Metal staircase attachment - no beam
(Gosh, I hope I'm describing this correctly..)
And if the weld doesn't fail in shear, then the weight of the stairs + live load is creating a load on the edge of the diamondplate, inducing a moment since the nearest support is several inches away. The diamondplate does have edge flanges which seems to be the only reason it has not bent already.
Thank you for the link, I'm reading through it now.
RE: Metal staircase attachment - no beam
Providing support through weld shear is common, but there are situations where it should not be done.
RE: Metal staircase attachment - no beam
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Metal staircase attachment - no beam
On the weld itself- shear strength is several thousand psi, so it doesn't take much weld to support a set of stairs if it's in the right place and the right configuration.
RE: Metal staircase attachment - no beam
RE: Metal staircase attachment - no beam
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Metal staircase attachment - no beam
It looks like the OSHA toeplate is formed up from a serious deck plate, and the diamond plate is a mere veneer over that.
If the stair stringer is welded to the end of the toeplate, it could be okay, unless the weld is as ugly as that between the bottom of the stringer and the deck edge.
OR, I could be completely misinterpreting what I'm not quite seeing.
Mike Halloran
Pembroke Pines, FL, USA
RE: Metal staircase attachment - no beam
The stair stringer is only attached to the diamondplate at bottom. The stair stringer at right is some 6" from the beam piece connected to the bottom set of stairs, and is about 6" forward of the small metal plate that connects the 2" hollow tubing frame to the diamondplate. The flange, or toeplate, is cut before the stair stringer and there is no attachment between that flange and the stringer.
On the left, the only connection is the 3" horizontal weld to the edge of the diamondplate.
I did have a laugh at "rogue stair genius", thanks.
RE: Metal staircase attachment - no beam
And yes, Mike's kick plate is your upturned "flange". Mike raises the excellent point that the floor landing appears to be made of two plates: a thicker plate on the bottom with a 4" upturn, and the diamond plate on the top with the 1.5" downturn. Can you confirm that? As Mike has alluded, it would seem logical for the designer to have intended for there to be a vertical weld connecting the toe plate to the end of the stringer.
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
RE: Metal staircase attachment - no beam
I can get a better picture from the top, but my memory says the toe plate isn't connected to the stair stringer at all and the only support on that stringer end is the weld visible in the photos.
This is actually the second poorly constructed staircase I've found at the same facility. The other featured the top of a staircase + platform supported only through shear on a weld about 3' wide. At the time I found it, the weld was cracking and daylight was visible through 1/3 of its length. I can post an Inventor file of that one... an emergency work order was issued and gussets were added the same night, but it too is using diamondplate as primary support. I was satisfied that the gussets prevented immediate collapse but I plan to recommend other modifications.
RE: Metal staircase attachment - no beam
Here is my opinion ( the preceding was not opinion ):
It looks marginally strong enough now.
It is unlikely that an inspector would fail it.
It is not likely to fail tomorrow.
In the future, when things corrode, get bumped and vibrated from use, I see trouble.
If it is in a high traffic area, I'd fix it RIGHT NOW.
If it gets used once in a blue moon, detail the fix and put it on the maintenance department's list of things to do.
Finally, pat yourself on the back for finding it, don't become jaded if the owner tells you to stuff it and keep your eyes and ears open!
RE: Metal staircase attachment - no beam
The stairs are holding up because they have not fallen down yet because only two lightweight people at a time have walked down the stairs while they are not carrying any load and have been quietly walking. NOT a building evacuation after an earthquake, fire, windstorm when the stairwell is loaded top-to-bottom with people rushing to evacuate because there is no elevator service!
Look again under the floorplate or decking. That decking becomes a "beam" because it has a turned-up 4 inch section on one side and a turned-down 2 inch section immediately under the stairs, right.
(Please! everybody QA me and my logic on this!)
But that bent deckplate is supporting half the weight of the next staircase riser we know for sure - and probably part of the next staircase turning platform, and maybe even part of the next riser section above that platform. There is no sign of additional structure, nor of how many more flights of stairs are being loaded through the force "track" from top to bottom.
Can the OP provide a photo of the entire stair?
But that platform that we do see is being held up by what looks like two angle iron point supports under it. So the load starts at the very far edge of the platform steel, is transmitted across the plate as a cantilevered beam with the stress being resisted by the 4 inch vertical "up" bent edge and the 2 inch bent "down" edge, and then that plate is being supported by two tiny angle braces about 24 - 30 inches away from the edge.
RE: Metal staircase attachment - no beam
Yes, this is exactly my concern. This staircase sees what I'd guess is "moderate" use (like you said, probably not more than 2 people at once, on the order of 10s of trips per hour).
There is one platform above which is beam supported, and where the staircase stringer is connected directly to the beam. There are no riser sections above this, fortunately.
I will go in this weekend and try to get more detailed photos.
That's mostly correct (the right idea at least), but there are at least 4 of these small angle iron point supports on this half of the platform. There are two nearer supports - one about 6" behind the right stair stringer, the other is about 12-16" behind and to the right of the left stair stringer. So the weight of the stairs + load on the corner of the plate is resting on cantilevered diamondplate. The diamondplate is only resisting the moment through the two flanges, which are about 4" and 1.5".
RE: Metal staircase attachment - no beam
As a minimum, there needs to be additional support directly from the column to the outside stair stringer.
Oh, by the way, do does this firm fabricate metal stairs for a business?
Mike McCann, PE, SE (WA)
RE: Metal staircase attachment - no beam
I agree, I don't really like the connection at right but it's the connection at left that mostly concerns me - both that the weld could corrode or fatigue and fail in shear, and that there is a more significant bending moment on the platform. I would guess that failure would occur if the 1.5" flange buckled at the edge in compression, because there is no attachment between the toe plate and the stair stringer.
RE: Metal staircase attachment - no beam
As IFRs and others noted, this is an awful detail. The weld used to fill the gap is somewhat of a fillet weld under both longitudinal and vertical shear. As Mike H. noted, if the stringer is welded to the toe plate, that helps.
The plate is cantilevered and under a typical required design load of 100 psf, the corner will exhibit a lot of deflection, thus twisting the poorly conceived weld even more. Not good.
A structural engineer needs to look at this and design a proper repair.
RE: Metal staircase attachment - no beam
I appreciate the comments here, it's nice to have my concern validated.
RE: Metal staircase attachment - no beam
RE: Metal staircase attachment - no beam
Connection detail, to settle the questions about thickness and the stringer connection to toe plate.
RE: Metal staircase attachment - no beam
The weld that's there is poorly profiled and not of good quality. In addition, it should have been cleaned and protected against corrosion.
Those stringers were shop fabricated. The landing looks like it was probably hatcheted and pieced together in the field.
Hopefully the structural engineer who looks at this will require it, but any repair welding should be done by a welder who is certified for structural welding and in the position for which the welding occurs. As an example, the photo shows an overhead fillet weld. This is a difficult position and the welder should show evidence of capability in this position.
RE: Metal staircase attachment - no beam
Mike McCann, PE, SE (WA)
RE: Metal staircase attachment - no beam
How many stair treads are on the stairway leading up from the platform?
Make sure you have permission to post photos like these, your boss/client may not appreciate it.
RE: Metal staircase attachment - no beam
I'm pulling the pictures down since i have the answer I needed - that it is worthy of bringing to the attention of a dedicated structural engineer, and that's what will be done.
Thank you all.
RE: Metal staircase attachment - no beam
gjc
RE: Metal staircase attachment - no beam
Faith is taking the first step even when you can't see the whole staircase. -MLK
RE: Metal staircase attachment - no beam
I will also direct his attention to another staircase I've become aware of, which has full thickness rust penetration on at least 2 surfaces of a box beam. I had no luck finding regulations on that either.
RE: Metal staircase attachment - no beam
With the exception of residential wood framing, structural codes and regulations tend not to be all that perscriptive about specific situations like that. They tend to require certain levels of safety and performance and give requirements on ways that you prove some of those things (i.e. how to calculate member capacities).
In straightforward plumbing and electrical for buildings you'll have a lot of details in the code that tell you exactly how you have to do specific things. Structurally, you can see the same basic thing done dozens of different ways in similar straightforward buildings, because it's at the discretion of the designer, how the load travels and where things are. Note: That's not to say that when you get to electrical and plumbing in more complicated scenarios they don't involve just as much engineering and expertise. They're just prescriptive over a much larger range than structural codes at the low end of building construction. That means you're much more likely to find a clause that tells you exactly how something must be implemented or maintained, while you're unlikely to find that in a general code for structures other than wood framed residential.