Voltage limits on motor terminals ?

Voltage limits on motor terminals ?

Voltage limits on motor terminals ?

(OP)
Dear all,

I am in search of information related to voltage operating limits in North America, more specifically switchgears and motor terminals.

ANSI C84.1 separates voltage limits in two categories, "service" and "utilization" voltages; but these refer to the voltage levels in buses throughout the system/industry (e.g.; switchgears); there is no mention of criteria for motor terminal voltages.

Please, is anyone aware of these ?

Thanks a lot,

Andre

RE: Voltage limits on motor terminals ?

Nominal system voltages. Nominal motor voltages.
120V ------------------------- 115V
240V ------------------------- 230V
480V ------------------------- 460V
2300V ------------------------ 2400V
4160V ------------------------ 4000V
In Canada
600V ------------------------- 575V

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Voltage limits on motor terminals ?

(OP)
Thanks Waross,

Please, do you have info about the voltage sag limit at the motor terminal bus when it starts ?

Thanks,

Andre

RE: Voltage limits on motor terminals ?

The minimum voltage at induction motor start has to assure a minimum motor torque -mainly the motor pull-up torque. Since the current decrease slowly from start up to breakdown torque the motor windings temperature will raise then the start duration has to be limited.
So, the acceleration torque-the difference between active torque the motor produces and the load torque-has to be enough to limit the starting time. The induction motor torque is- approximately- direct proportional with the supply voltage then the minimum voltage has to assure a limited start time.
Then the minimum starting voltage depends on starting type: D.O.L., delta-star, VFD or else [the starting current could be 6-8 times the rated for D.O.L. and close to rated for VFD]; load torque type: fan, centrifugal pump, compressor, lift, conveyor and other; the inertia moment of the motor and of the load and other parameters. Usually in low-voltage world the small motor permits dip voltage drop but big one less [usually up to 30% for small one and 10% for a big motor].

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources