Transformer charging with Generator
Transformer charging with Generator
(OP)
Hi,
Can anyone throw some light on the long term impact on the generator,energizing the transformer?
A 5 MVA 33/11kV Transformer needs to be charged with a 10MVA,11kV Steam Turbine Generator.Is there any thumb rule for Generator-Transformer charging?
Can anyone throw some light on the long term impact on the generator,energizing the transformer?
A 5 MVA 33/11kV Transformer needs to be charged with a 10MVA,11kV Steam Turbine Generator.Is there any thumb rule for Generator-Transformer charging?





RE: Transformer charging with Generator
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Transformer charging with Generator
I do agree with your recommendation.But in practice it is not always possible to charge the transformer with the generator directly connected as a single unit.Hence I am wondering is there a cut off limit by which we can design and operate plant electricals,which will be of some guideline.
RE: Transformer charging with Generator
You may consider pre-charging,- That is energizing the transformer through current limiting resistors and then shorting out the resistors.
I seem to recall also some discussion of a method to reduce the residual magnetism when a transformer is de-energized to avoid the worst case asymmetrical energization surges.
Bill
--------------------
"Why not the best?"