POINT IO with a CompactLogix (RSLogix5000)
POINT IO with a CompactLogix (RSLogix5000)
(OP)
I'm using for the first time POINTio consisting of an ethernet module 1734-AENT and a 1734-OA2 and two 1734-IN4.
Within RLSlogix5000, I've added the 1734-AENT under the IO config and ethernet. But I do not seem to either find where the actual IO modules are added, or even addressed. (BTW this is my first time using RSlogix5000 as well with a compactlogix PLC). Any links to examples or pointers?
Within RLSlogix5000, I've added the 1734-AENT under the IO config and ethernet. But I do not seem to either find where the actual IO modules are added, or even addressed. (BTW this is my first time using RSlogix5000 as well with a compactlogix PLC). Any links to examples or pointers?





RE: POINT IO with a CompactLogix (RSLogix5000)
http://literature.rockwellautomation.com/idc/group...
Right click on AENT and select module.
RE: POINT IO with a CompactLogix (RSLogix5000)
RE: POINT IO with a CompactLogix (RSLogix5000)
So I have two modules physically connected to the AENT module, and Ethernet tied to the PC and using the web browser I can get access to it. When I scan for attached modules, it cant find them at 0 and 1, but now I see they are sitting at 62 and 63? Seriously? I see NOTHING about setting slot addresses for these units. RSlogix500 only allows me to set a chassis size of 4, so no wonder it cant see these modules out there.
Any ideas on how to set these modules addresses?
Status LEDs on the AENT has the point bus flashing red, and the two modules network status flashing green.
RE: POINT IO with a CompactLogix (RSLogix5000)
Now onto the next issue...