500 kV GIS has been type tested on 60 Hz, would it be ok on 50 Hz operation or I need to recommend retesting?

RE: 500 kV GIS type tested @ 60 Hz

I would look for test passes against all relevant standards. There are IEC equivalents to (presumably) the ANSI standards.

If the manufacturer doesn't want to play ball then take them off the bid list. Most TSO's will be fairly prescriptive about what they will connect to their system, so even if you don't reject it I expect that the TSO might well do so.

RE: 500 kV GIS type tested @ 60 Hz

I had experience with circuit breaker SF6-50 Hz 230kV replacing 230kV breaker SF6-60 Hz.
The only type test that it is not tended refers to maneuvers with capacitive loads.





Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources