generator hunting
generator hunting
(OP)
I have problem of generator 2500KVA hunting on load, when not on load is not hunting.
Few parts;
Woodward DSLC -2
UG-Actuator Woodward part number A8251-724
2301A Speed Control
Few parts;
Woodward DSLC -2
UG-Actuator Woodward part number A8251-724
2301A Speed Control





RE: generator hunting
Fuel too light a grade??
Overloaded??
Air leak in the fuel line?
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generator hunting
Play in the governor linkage?
RE: generator hunting
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generator hunting
Maybe you can address the questions above and add some more details of your unit and system, then you can likely get better answers.
Mike L.
RE: generator hunting
Sticktion in the actuator.
Bad AVR.
Fuel starvation.
Improperly adjusted stability adjustment on the AVR.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: generator hunting