generator hunting

generator hunting

generator hunting

(OP)
I have problem of generator 2500KVA hunting on load, when not on load is not hunting.
Few parts;
Woodward DSLC -2
UG-Actuator Woodward part number A8251-724
2301A Speed Control

RE: generator hunting

Fuel filter needs changing??
Fuel too light a grade??
Overloaded??
Air leak in the fuel line?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: generator hunting

Governor gain too high?
Play in the governor linkage?

RE: generator hunting

Sticktion in the governor or the actuator linkage?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: generator hunting

Can you provide some details about your unit and controls? A 2301A and a DSLC2 sounds like a recent retrofit. is that the case? Is this a problem with a new or recently changed unit, or a new problem on an existing unit? Since you have a DSLC2 I'm guessing you are paralleled to something else, correct? What?

Maybe you can address the questions above and add some more details of your unit and system, then you can likely get better answers.

Mike L.

RE: generator hunting

I have had generators hunting from:
Sticktion in the actuator.
Bad AVR.
Fuel starvation.
Improperly adjusted stability adjustment on the AVR.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: generator hunting

I've had a generator hunt while starting large motors with soft starters. The solution was to lower the governor gain setting on the generator controller.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources