Harmonic Currents in a Capacitor Bank

Harmonic Currents in a Capacitor Bank

Harmonic Currents in a Capacitor Bank

(OP)
Hi all,

Just a general protection question. I am tasked with sizing CTs for a 275kV C-filter H-configuration capacitor bank. And since we are on a pretty tight budget, I am wondering if it is necessary to take into account the harmonic currents when sizing my LV CTs? I am unsure if most relays out there would even pick them up (Siemens/ABB/etc).

Greatly appreciate your input. Thanks!

RE: Harmonic Currents in a Capacitor Bank

Generally speaking, the total continuous current shouldn't be greater then the primary rating of the CT.

RE: Harmonic Currents in a Capacitor Bank

Some other things to perhaps consider

I would also check on the filtering capabilities of the protection relays. This should not be really be a concern with modern numerical relays but can pose a problem with older static type relays that may be using basic filtering techniques. Secondly I not sure what protection functions you are opting for but then again if you are buying a specific capacitor protection relay it should incorporate a comprehensive suite of generic functions. I would agree with LionelHutz in terms of the ratio and nominal current but bare in mind there are also effects like inrush current (rich in harmonics)and ct saturation. These can be overcome by point on wave switching devices and proper ct core type selection. Furthermore one could introduce a damping reactor in the bank to limit the inrush current.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources