I am using Trane Trace 700 to model three alternative mechanical systems. I have tried to keep all of the envelope, ventilation, lighting, and internal loads the same between the alternatives, to focus on the energy and economic effect of the different mechanical system choices. For this, the Rooms and Templates for Alternatives 2 and 3 are using the information entered in Alternative 1. After calculating, Alternatives 2 and 3 have receptacle loads that are identical to each other, and higher than the receptacle loads in Alternative 1. I have looked through the "entered values" reports, and cannot find any differences in the internal or miscellaneous loads between Alternative 1 and 2/3. Does anybody have any ideas about why the receptacle loads should be different between the alternatives if the same templates and room definitions were used?





RE: Different receptacle loads between alternatives using Trace 700
Call Trace support, that is free with your subscription. If they can't help over the phone, you also can send them your archived "taf" file, they typically have 1 day turnaround for that.
RE: Different receptacle loads between alternatives using Trace 700
RE: Different receptacle loads between alternatives using Trace 700
If any of the alternates include an energy recovery fan, the "parasitic load" to run this fan is added, in the energy summary reports, to the "Receptacles" category. After calculating, in "Detailed Reports", select "Equipment Energy Consumption". There will be data for each alternative. Any alternatives that include energy recovery will have a heading labeled "Energy Recovery Parasitics". In the summary reports, this amount is simply added to the "Receptacles" load. This explains (one way at least) how you can have different "Receptacles" loads for identical template and room definitions.
RE: Different receptacle loads between alternatives using Trace 700